ag_pete09 said:
Nice, that's what I was thinking about doing as well.
Two issues for me are getting the power outside or the cord inside (breaker is inside garage midway to garage or back door with brick on back) and making room for the generator breaker.
I figured out I could possibly use my dryer breaker as I have a gas dryer and it works without it. Or I could change some breakers to tandems and shuffle a few around and down.
Here's my breaker. Any thoughts on which is a better route? Disconnect dryer or shuffle?
![](https://f5s-img.s3.amazonaws.com/000/55/42/554231beb4ca2dc1ae379c6b306d0846973f7b77_3112564_u101843.jpg)
Pretty sure this is the interlock for your panel:
Eaton KitThe problem is that your box is full. If you wanted to use your dryer breaker you would still have to move it. The interlock kit needs the Gen breaker to be the top double pole on the left where your A/C circuit is. You might be able to double up some of the circuits you have to make room in your panel. Your "microwave" and "vent hood" are two circuits that stand out to me. Unless you have a giant one of each there is no reason they cannot be on the same circuit. My Generator inlet is on my brick wall behind my panel. Installation is pretty easy, might need to do a little drywall work though.
Not sure about removing the power to the gas dryer though. Does it use any power for timers/ buzzers etc?
Edit: After looking back at your picture I see that your dryer breaker is off so that might be the best option. Cap the wires off in the panel and label them, swap sides with the a/c breaker, install interlock kit and generator inlet and you should be good to go.