I just returned from the 78th annual relay conference at Texas A&M. This conference was started in 1948 as a way for electrical engineers to collaborate on the best way to design and set protection relays for generators, transmission and distribution lines, and industrial loads.
The past couple of years has been dedicated to how to deal with inverter based resources (IBRs). These are generating units that rely on inverters for generation (solar, wind, and battery storage). The problem with inverters is they do not act in a predictable fashion like synchronous machines (turbine generators).
If there is a fault on the system, synchronous machines slow down gradually, provide a lot of fault current, and provide predictable "signatures" in the fault current so that relays are able to detect the fault and isolate it with minimal loss to electric customers.
Inverters do not do this. They rapidly change frequency to protect themselves, provide very little fault current, and do not provide a "signature" so that our relays are not able to distinguish a true fault from normal load current. This is a problem because the relays may not trip breakers when they need to. Or they'll trip when they're not supposed to.
If you look at the papers from the past three years, about 1/3 - 1/2 are dedicated to this problem and proposals to how to solve it.
https://na.eventscloud.com/website/78210/archive/
From listening to the presentations this week, it can be summed up from one such presentation by PG&E.
https://na.eventscloud.com/file_uploads/c215cc72a075d4060a5016e0e13df5c7_1-EventAnalysis-InnovativeToolsandStrategiesforProtectionEngineers.pdf
The relevant section is about half way down: Inconsistent IBR Fault Current Contributions. We may do our best to come up with a way to model IBRs and set our relays in a way we think they will behave. But this was a real world example of the SAME inverter during two faults behaving in two entirely different manners.
I believe the US is due for a regional blackout and it will be caused by this issue. One of the last papers yesterday was by Entergy presenting on line protection solutions for IBR interconnections.
https://na.eventscloud.com/file_uploads/b8e0753fbd9fe32e19801d92f3b48c7f_4-LineProtectionSolutionsforMultipleIBRInterconnectionsinanIncumbentUtilityInfrastructure.pdf
In passing they mention they are moving from 2% renewables in 2023 to 25% by 2030. As it stands, we have sufficient synchronous machines with enough inertia for the relays to see and isolate faults, but unless we require inverter manufacturers to design their products to address this issue, we're going to have a problem when more of these are connected to the grid.
The past couple of years has been dedicated to how to deal with inverter based resources (IBRs). These are generating units that rely on inverters for generation (solar, wind, and battery storage). The problem with inverters is they do not act in a predictable fashion like synchronous machines (turbine generators).
If there is a fault on the system, synchronous machines slow down gradually, provide a lot of fault current, and provide predictable "signatures" in the fault current so that relays are able to detect the fault and isolate it with minimal loss to electric customers.
Inverters do not do this. They rapidly change frequency to protect themselves, provide very little fault current, and do not provide a "signature" so that our relays are not able to distinguish a true fault from normal load current. This is a problem because the relays may not trip breakers when they need to. Or they'll trip when they're not supposed to.
If you look at the papers from the past three years, about 1/3 - 1/2 are dedicated to this problem and proposals to how to solve it.
https://na.eventscloud.com/website/78210/archive/
From listening to the presentations this week, it can be summed up from one such presentation by PG&E.
https://na.eventscloud.com/file_uploads/c215cc72a075d4060a5016e0e13df5c7_1-EventAnalysis-InnovativeToolsandStrategiesforProtectionEngineers.pdf
The relevant section is about half way down: Inconsistent IBR Fault Current Contributions. We may do our best to come up with a way to model IBRs and set our relays in a way we think they will behave. But this was a real world example of the SAME inverter during two faults behaving in two entirely different manners.
I believe the US is due for a regional blackout and it will be caused by this issue. One of the last papers yesterday was by Entergy presenting on line protection solutions for IBR interconnections.
https://na.eventscloud.com/file_uploads/b8e0753fbd9fe32e19801d92f3b48c7f_4-LineProtectionSolutionsforMultipleIBRInterconnectionsinanIncumbentUtilityInfrastructure.pdf
In passing they mention they are moving from 2% renewables in 2023 to 25% by 2030. As it stands, we have sufficient synchronous machines with enough inertia for the relays to see and isolate faults, but unless we require inverter manufacturers to design their products to address this issue, we're going to have a problem when more of these are connected to the grid.