Adding ridge vents where there are gable vents is not recommended, as the air just "short circuits" from the gable to the ridge.
The currently-accepted formula is 1/150. Where you divide the floor area of the entire attic by 150. Thus, for 3200 sf of attic, you'd 3200 ÷ 150 = 21.33 square feet. half of that to be intake, half exhaust. Typical ridgevent is 18 square inches per lineal foot. Our putative 21.33 / 2 is 10.66 * 144 = 1536 sq. in., or about 84 lineal feet of ridgevent.
Those rectangle vents are only about 56 sq.in. each--28 in out example. Continuous soffit vents run from 12 to 120 sq.in. per foot.
However, Building Science research shows that the 1/150 ule is about like rolling your car windows down two-fingers' worth. Like rolling down the windows in your car 1-3/4 to 2" there is some effect, about 4-5º temperature reduction. In Texas, 1/150 attic ventilation produces the same result, 4-5º temperature cooler. So, instead of hitting 140º you attic drops to a frigid 135º
Given how much infrastructure we run in the attic, it's really a lot better to extend the insulation plane up the walls and under the roof. In retrofit this introduces a need for changing how combustion air is supplied, but that is a surmountable detail. One very much offset by not having ventilation ducts in 130º attics (that R5-6 blanket is only keeping the duct air down to 124-126º).