I have a sauna heater with a 220V plug but of course I'm set up for a typical 120V outlet. Does anyone have a recommendation out a converter box or process. I have zero electrical ingenuity so a simple converter would be best.
akaggie05
How long do you want to ignore this user?
AG
While it's technically possible to use a transformer to step 120v up to 240v, this is not likely going to be feasible in your application due to the current draw (likely higher than what a standard 15 or 20A 120v circuit can provide) that would be required to service an appliance made to run on 240v. Can you post a picture of the label from the heater that shows amps or wattage?

Better solution is most likely going to be to run a new 240v circuit from your breaker panel with correctly sized wire and proper receptacle.

Edit (more direct explanation):
Voltage and amperage are inversely proportional when calculating total power delivery. If the heater (for example) needs 15 amps at 240 volts, it would need 30 amps at 120 volts (which would be too much current by upwards of 2x what a standard 120v circuit in your house is set up to provide). You would need to upsize the wire gauge and install a higher capacity 120v breaker, and by that point you may as well just run a new 240v circuit with thinner wire for the lower current.
rooftop18403
How long do you want to ignore this user?
https://www.vevor.com/sauna-heater-stove-c_10155/vevor-sauna-heater-9kw-220v-electric-sauna-stove-steam-bath-sauna-heater-with-built-in-controls-3h-timer-and-adjustable-temp-for-max-317-459-cubic-feet-home-hotel-spa-shower-use-p_010676999828?adp=gmc&utm_source=google&utm_medium=cpc&utm_id=17002292636&ad_group=&ad_id=&utm_term=&gad_source=1&gclid=Cj0KCQiAvbm7BhC5ARIsAFjwNHs9I6***wlP3Zy9Z65A6fvlhl42-M4K2rXdK0sgfbwwM257SVBSMgsaAnu8EALw_wcB

I'm just trying to plug this into the wall...
akaggie05
How long do you want to ignore this user?
AG
Yeah, assuming you're looking at the 9kW (9000 watt) version, there's not going to be any plugging that into a standard 120v outlet, even with a transformer. 9000 watts at 240 volts is 37.5 amps, which puts you roughly into the territory of a circuit for an electric range or wall oven. You need to get a new 240v circuit installed with the correct wire (likely 8 or even 6 gauge) and appropriately sized breaker.
jg07
How long do you want to ignore this user?
AG
Just to reiterate this, at 120V, 9000W is 75A. You're not setup for that. At best you're probably wired for 20A at your 120V receptacle. Most builders will throw that on a 15A circuit unless you dedicated it specifically for something more.

You might as well run a 50A, 240V circuit rather than messing around with a transformer. How far are you from your panel?
rooftop18403
How long do you want to ignore this user?
Not far. I have a 120v receptacle near the would-be heater and the actual breaker box is in the same room less than 15' away. How easy would a receptacle switch be?
jg07
How long do you want to ignore this user?
AG
rooftop18403 said:

Not far. I have a 120v receptacle near the would-be heater and the actual breaker box is in the same room less than 15' away. How easy would a receptacle switch be?
If they have an easy path to the panel its not hard.
Sweet Kitten Feet
How long do you want to ignore this user?
S
Just call an electrician and get it done the right way. And next time check before buying of your current setup can accommodate an appliance like that.
Col. Steve Austin
How long do you want to ignore this user?
AG
jg07 said:

Just to reiterate this, at 120V, 9000W is 75A. You're not setup for that. At best you're probably wired for 20A at your 120V receptacle. Most builders will throw that on a 15A circuit unless you dedicated it specifically for something more.

You might as well run a 50A, 240V circuit rather than messing around with a transformer. How far are you from your panel?
Not to mention that a step-up transformer that could power that heater would be prohibitively expensive. Cheaper to just hire an electrician as has been suggested.
I am not the Six Million Dollar Man, but I might need that surgery. "We have the technology, we can rebuild him!"
Col. Steve Austin
How long do you want to ignore this user?
AG
OP - any update?
I am not the Six Million Dollar Man, but I might need that surgery. "We have the technology, we can rebuild him!"
Refresh
Page 1 of 1
 
×
subscribe Verify your student status
See Subscription Benefits
Trial only available to users who have never subscribed or participated in a previous trial.