Rattler12 said:
Would this be safe or even solve OP's problem? A 100 amp breaker in the shop trying to pull 70 or larger amp load from the shop equipment is just going to result in the 60 amp house breaker tripping. He'd need 100 amp breaker in each box and is the current wiring from the house 60 amp rated at handling 100 amps ?????
I could have written more clearly, but I don't think you and I are talking about the same breaker.
Current set-up: A 60A Feeder breaker in house main panel supplies power to a 60A Main breaker in a subpanel in shop. The subpanel in the shop has other feeder breakers, but I'm not considering those.
Proposed set-up: A
70A Feeder breaker in the house main panel supplies power to a
100A Main breaker in the subpanel in the shop. Subpanel itself needs to be rated for >60A and cable between the house and subpanel needs to be #4 AWG or greater
If the panel rating and cable size allow for it, then you can upgrade both breakers to allow for 10A more capacity, which definitely could solve OP' s problem. Only one of the two breakers needs to be sized to protect the cable between the house and shop. It depends on the brand of the subpanel, but it's unlikely that the subpanel main can be upgraded to 70A (I'm guessing 100A is more readily available). But for the feeder breaker in the main panel in the house, a 70A breaker is likely to be more readily available. If the subpanel itself isn't rated for >60A, or the cable is smaller than #4, then this is moot and other options will need to be considered