Have a 4 yo Lennox High Efficiency furnace vertical interior install drawing combustion air in through the roof in the combo roof stack vent. Model EL296UH090
Toward the end of the 22 winter it would occasionally throw an error for not igniting on demand. Cycling the power switch fixed it.
Last winter, toward the end of the season it became worse. Would throw an error for open low pressure switch. Replaced the pressure switch and checked the different vacuum lines and limped to the end of the winter. By the end it was not coming on, but I didn't have time to mess with it and decided to wait until now.
Started messing with it when it cooled off a couple weeks ago Replaced the pressure switch again because it kept throwing E223 and E229. While messing around I noticed/realized that the induction motor was never coming on but that it was getting warm. Google suggested there might be debris in there. Since this had now become a personal challenge to my ME background, I plunged ahead and ordered a new induction motor assembly.
Replaced it today. Furnace fired right up upon reassembly. So presumably, that was the main problem. Really easy job, except that they made it hard by the way they installed the gas pipe.
Expected that I would find all kinds of crap down in the old motor, perhaps from an installation issue. But it was perfectly clean. The impellor did seem possibly, slightly "stuck" when I first touched it. But it broke loose easily and spun freely. I cannot say if it possibly had water build up at some point, as it hasn't rained in a month.
Now I am happy I got it fixed, but stumped on exactly what caused it to fail. Somewhat leaning to just a bad part from the factory. I occasionally see new and one year old furnaces where the induction motor is making awful sounds on inspections. But still wonder if there is some installation problem. Mainly, that due tot he vertical installation, the motor housing is the lowest point of the exhaust system, and if water did get into that housing it has nowhere to go. Googling tech forums suggested some installations have a drain fitting at the lowest point. There is even a little nipple that could be for that, but it is not open. I am not comfortable punching holes....
Any thoughts?
Toward the end of the 22 winter it would occasionally throw an error for not igniting on demand. Cycling the power switch fixed it.
Last winter, toward the end of the season it became worse. Would throw an error for open low pressure switch. Replaced the pressure switch and checked the different vacuum lines and limped to the end of the winter. By the end it was not coming on, but I didn't have time to mess with it and decided to wait until now.
Started messing with it when it cooled off a couple weeks ago Replaced the pressure switch again because it kept throwing E223 and E229. While messing around I noticed/realized that the induction motor was never coming on but that it was getting warm. Google suggested there might be debris in there. Since this had now become a personal challenge to my ME background, I plunged ahead and ordered a new induction motor assembly.
Replaced it today. Furnace fired right up upon reassembly. So presumably, that was the main problem. Really easy job, except that they made it hard by the way they installed the gas pipe.
Expected that I would find all kinds of crap down in the old motor, perhaps from an installation issue. But it was perfectly clean. The impellor did seem possibly, slightly "stuck" when I first touched it. But it broke loose easily and spun freely. I cannot say if it possibly had water build up at some point, as it hasn't rained in a month.
Now I am happy I got it fixed, but stumped on exactly what caused it to fail. Somewhat leaning to just a bad part from the factory. I occasionally see new and one year old furnaces where the induction motor is making awful sounds on inspections. But still wonder if there is some installation problem. Mainly, that due tot he vertical installation, the motor housing is the lowest point of the exhaust system, and if water did get into that housing it has nowhere to go. Googling tech forums suggested some installations have a drain fitting at the lowest point. There is even a little nipple that could be for that, but it is not open. I am not comfortable punching holes....
Any thoughts?