I bought a house last summer that's a bit smaller than 2100 sq.ft. It had the original HVAC system which, like the house, was 18 years old. I replaced it last fall with an American Standard system.
Both units were/are 4 tons, despite the fact that my HVAC's company salesman supposedly did a heat load calculation and said I could get by with 3.5 tons.
Once it got hot this summer, I found that the new unit couldn't keep up with temps over 95. Additionally, my layman's measurements of the temperature drop of the supply vent closest to the attic unit and the return was only 11-13 degrees. So the HVAC company sent some guys out yesterday to check on it. They found out that the fan was set for a 5 ton unit so they changed the switches to a 4 ton and added additional refrigerant.
Their changes have helped a lot but not as much as I was hoping. They measured the delta-T right at the coils and got only an 18 degree difference. Is that about right or should it be more? The delta T between the return and the supply vent inside my home is now about 15-17, which seems to be the bare minimum. The system can now very slowly cool my house until outside temps get to ~99 or so.
I was expecting better numbers than that given it's a new system and slightly oversized (supposedly) for my house. Are my expectations unrealistic? If not, what else can I do; what are my options?
Thanks, guys.
Both units were/are 4 tons, despite the fact that my HVAC's company salesman supposedly did a heat load calculation and said I could get by with 3.5 tons.
Once it got hot this summer, I found that the new unit couldn't keep up with temps over 95. Additionally, my layman's measurements of the temperature drop of the supply vent closest to the attic unit and the return was only 11-13 degrees. So the HVAC company sent some guys out yesterday to check on it. They found out that the fan was set for a 5 ton unit so they changed the switches to a 4 ton and added additional refrigerant.
Their changes have helped a lot but not as much as I was hoping. They measured the delta-T right at the coils and got only an 18 degree difference. Is that about right or should it be more? The delta T between the return and the supply vent inside my home is now about 15-17, which seems to be the bare minimum. The system can now very slowly cool my house until outside temps get to ~99 or so.
I was expecting better numbers than that given it's a new system and slightly oversized (supposedly) for my house. Are my expectations unrealistic? If not, what else can I do; what are my options?
Thanks, guys.