quote:
I had forgotten to mention I "fixed" the AC problem I was having while back by bypassing the pressure switch in line with the compressor and adding more Freon... it seems that the switch is bad, and I also have a slow freon leak, maybe.
ACK! Normally that low pressure switch cuts off the compressor when the suction side pressure gets too low. This should happen intermittently even with a proper charge of refrigerant in all but the hottest/humidest conditions. If you're low on freon, and you've bypassed the switch, the compressor will just keep right on running and freeze up the evaporator until it's a giant block of ice, and air can't pass through it. Still feeling cold air at the vents, but the flow gradually slows and stops? Classic symptom of evaporator freeze up.
You need to remedy this quick or you will have a bad compressor very soon. Aside from preventing freeze up when refrigerant levels are low, the low pressure switch is designed to protect the compressor. The refrigerant carries the compressor's oil through the system. When the suction side pressure gets too low, there might not be adequate refrigerant flow to carry oil to the compressor sufficient to keep it lubed. That means the compressor is in danger of starving for oil. A bypassed low pressure switch will make the compressor keep right on running to its early demise.