slab question - fiber reinf. or rebar

1,888 Views | 15 Replies | Last: 2 yr ago by Aggietaco
cavscout96
How long do you want to ignore this user?
AG
28 x 28 garage slab

60% @ 4"
40% @ 6" for eventual two post lift

trying to decide on traditional rebar or fiber reinforced.

looking for thoughts or experiences; pros / cons.

Aggietaco
How long do you want to ignore this user?
AG
Are your costs the same and do you have engr design for both methods?

If so, I would lean towards fiber, especially for future mounting of equipment if you aren't doing embeds for the lift. That way you don't have to worry about drilling through bar when you set your posts.

Theoretically, you will have less superficial cracking as well, so if you are using a urethane/polyurea/epoxy coating, you will have less surface issues.
TexAg1987
How long do you want to ignore this user?




Quick answer: Fiber Mesh or Rebar? - Fiberego


tgivaughn
How long do you want to ignore this user?
AG
Any lift ideas deserve either a structural engineer or surgeon
+ fiber only helps rebar, never replaces it in structural apps
Ten words or less ... a goal unattainable
cavscout96
How long do you want to ignore this user?
AG
the lift manufactures spec min 4 1/2" reinforced (fiber or rebar) at a min compressive strength of 3k psi

I'm planning 5 1/2" read the article. looks like I'll be tying rebar....

Thanks
Whoop Delecto
How long do you want to ignore this user?
AG
cavscout96
How long do you want to ignore this user?
AG
Not looking to save $$ per se, but more the time and effort (mostly time) jacking with rebar placement and tying. After more research, looks like fiber is more for surface cracks and structural use really needs rebar, so... bar it is
Aggietaco
How long do you want to ignore this user?
AG
I've poured a lot of (like 1.5MM+ SF) SOG with 4#/CY of fiber and no bar with some fairly high DL/LL capacities...
Whoop Delecto
How long do you want to ignore this user?
AG
Are the floors fuzzy? Can you see fibers with vehicle headlights at night?
southernskies
How long do you want to ignore this user?
Fiber is better suited for topping slabs with minimal slab thickness. I wouldn't even give it a thought.
Aggietaco
How long do you want to ignore this user?
AG
Whoop Delecto said:

Are the floors fuzzy? Can you see fibers with vehicle headlights at night?
If you finish the slab, the trowels will remove or push down any of the fiber tails that stick up. The only areas you'd have to address are around penetrations are close to walls where you wouldn't work the slab as much. Even then, a pear burner takes care of them easily.
cavscout96
How long do you want to ignore this user?
AG
Aggietaco said:

I've poured a lot of (like 1.5MM+ SF) SOG with 4#/CY of fiber and no bar with some fairly high DL/LL capacities...
tell me more...... application? soil types? subgrade prep? which type of fiber? poly?
Aggietaco
How long do you want to ignore this user?
AG
cavscout96 said:

Aggietaco said:

I've poured a lot of (like 1.5MM+ SF) SOG with 4#/CY of fiber and no bar with some fairly high DL/LL capacities...
tell me more...... application? soil types? subgrade prep? which type of fiber? poly?
Manufacturing plant 8" SOG although I'm about to do some in a few weeks at an athletics facility as well but that is a topping slab, not a structural slab. Soil type at the previous job was garbage on-site curated fill but installed correctly in lifts. That project was Euclid Tuf Strand but we also entertained a micro steel product from Helix until we determined it would interfere with some of the clients sensitive operations. If you aren't looking closely at the finish around the columns, you can't tell it's not a traditionally reinforced slab.
62strat
How long do you want to ignore this user?
AG
Aggietaco said:

I've poured a lot of (like 1.5MM+ SF) SOG with 4#/CY of fiber and no bar with some fairly high DL/LL capacities...
4 lbs per cy??

I've done a 4" fiber floor for ProLogis, (using concrete fiber solutions), approx 200ksf, spec was 66 lbs per CY.

4 pounds/cy seems like hardly anything.
only 4 construction joints (50ksf pours), and sawcuts split those joints, plus down the long dimension, so joints were 100x100.
Not totally jointless.
CEPhD
How long do you want to ignore this user?
AG
Soil prep is more important than either.
Aggietaco
How long do you want to ignore this user?
AG
Yes, 4# in a 4000 mix. We did 5-600 yard pours to be able to get off of them the same day and were turning 3-4/week at peak, so 20-25k sqft. Column bays were 14m x 14m and we cut that in thirds for joints.

I looked back at the Euclid data and their dosage ranges from 3# to a max of 20#. I can say, we had hardly any shrinkage cracks, and not having to pump or make a path for trucks in the rebar mat was a great time saver. Just had to leave an opening in the edge form and back trucks in as quick as the plant could turn them.