So installing thermostats in my house we just bought. 3 units. 3 thermostats. Installed the first two no problem. Have a question about #3, which is upstairs.

The other two were both RH, G, C, Y and W and the one i have a question about has its yellow wire going into Y2 as opposed to Y which doesn't show as a "valid configuration" when I input it into the installation app. I click "next" and the app says "please select a valid configuration". Should I just put my yellow wire into "Y"?

Screen shots of my new thermostats, the current wiring on the old thermostat which I found, and the screenshot from the app.


VAXMaster
How long do you want to ignore this user?
AG
Need to see what that yellow wire connects to on the other end but the Y2 terminal is for second stage cooling on a two stage unit. Assuming your system is a single stage the yellow wire should just go to Y, not Y2.
RikkiTikkaTagem
How long do you want to ignore this user?
AG
Section327Ag said:

Need to see what that yellow wire connects to on the other end but the Y2 terminal is for second stage cooling on a two stage unit. Assuming your system is a single stage the yellow wire should just go to Y, not Y2.


Let me see if I can figure out if it's a two stage system. There's 3 units so I'll see which one connects to this system. I'll be out of town a couple of days and see.
Refresh
Page 1 of 1
 
×