southernskies said:
Pretty sure commercial electric code allows up to 80% load on any given circuit. so max load allowed on a 20A circuit is 16A. I would try to stick to this rule to be safe. You don't want to be running at 19A all day every day. Your conductors will stay hot and could potentially lead to a fire.
The 80% only applies to continuous loads, defined as anything running continuously for three hours or longer - not plugged in or turned on,but actually running. Lights are continuous. Fridges ae not. The 80% number is kinda/sorta the backwards way of looking at the requirement. The overcurrent protection, in this case a circuit breaker, has to be sized to 100% of non-continuous loads plus 125% of continuous loads. So if you had all continuous loads, you could only go up to 80% of the breaker.
That's just the breaker, however. Fridges are motor loads. The wire has to be sized for all the loads plus 25% of the largest one. If your fridge is truly 12A, you'd have 12A + 2.1A + 3A = 17.1A. You'd need to have #12 wire which *should* correspond to the 20A breaker if installed as it should.
Being a motor load also means there is a starting inrush. A 12A fridge might spike to 18-20A when starting. If both fridges started at the same time you could have a nuisance trip.
I'd double check the load of your fridge.